I'm pleased the diodes are the correct way. Thanks for the confirmation. The second statement is interesting and maybe problematic. I hoped that the Ecoflow would charge via solar during the day and then at night the 12v input (car cigarette charger) would take over. But I have tested at night (no sun) and the PV circuit is still 45V. If this is the case (and from your statement) the 12v input will never contribute. I will test this, but I don't want to connect it up until I am sure that the 12v circuit is protectedThe photo appears to show the diodes arranged correctly for the lower connector to be the output and the upper two as alternate inputs.
As long as the voltage from the solar panels is higher than the battery voltage, the battery will not contribute any current as its diode will be reverse biased.
(And presumably by the solar panel output drops below 15V, the current available from them will be pretty low).
Thank you for your time and help also you are helping me to think through this.If that portable battery station has a connector that accepts 10 to 65 VDC input; you need nothing to connect such unit to a 12V battery or to a solar panel that yields 40VDC but not both.
If the charging method switch is part of the Ecoflow controls, select depending what source you connect.
If what you want is to have both permanently connected and not select the switch for the working source or swapping cables, you must use the DC-to-DC converter and leave the switch in 12VBat position.
40VDCSolarpanel----------->DCconverter---------->12Vbattery------------->Ecoflow--------->Itsoutletsofchoice
That way no matter what supplies the Ecoflow, it will always be 12VDC from the battery being charged or not by the solar panel at that moment.
Be aware that 12VDC to supply 1KW; the current would be 83 Amperes which I doubt that connector XT60 can handle. Is there a battery inside the Ecoflow ?
Having the diodes as seen on your image will not allow the battery at XT60 to receive charge from the solar panel.
Diodes conduct when forward biased and do not conduct when reversed biased. I see that you understand this. But it means you will see a small forward voltage, a few hundred millivolts, if you measure the voltage across the diode when it is forward biased. But when it is reverse-biased, you will not see zero. That would mean it was a dead short. You will see whatever voltage would be present in the circuit if the diode was missing completely. In your case, this is the solar panel open-circuit voltage minus the battery voltage. Likely tens of volts.
It's simply your 'reading' of the meter that is at fault - the meter won't be reading '0' - it will be displaying an over-range indication.So this means that my logic and use of multimeter is incorrect? (course by lack of knowledge)
I used the diode setting to check the orientation, a few millivolts one way, 0 the other.
Indeed I am picking up the open-circuit voltage on the reverse side, I thought this was a problem with the diode but it seems this is normal from how you describe (how diodes work)
hoped that the Ecoflow would charge via solar during the day and then at night the 12v input (car cigarette charger) would take over. But I have tested at night (no sun) and the PV circuit is still 45V. If this is the case (and from your statement) the 12v input will never contribute. I will test this, but I don't want to connect it up until I am sure that the 12v circuit is protected
You cannot "simply diode OR" 45V and 12V together on the same wire and expect MPPT PV charging.
You can feed the "Ecoflow Delta" unit with that setup, though, to continue to put some charge in to it.You cannot "simply diode OR" 45V and 12V together on the same wire and expect MPPT PV charging.
Correct. Fuse is 10AI assume the car charger is Fuse protected for >=10A and the DELTA will not demand more than 8A at car battery voltages.
I thought the diode provided reverse voltage protection.I do not see any reverse voltage protection for the PV panel at night when the PV output is lower than the car charger. I assume that is the diode you are using which should be rated for 15 A to 25A for lower temperature rise than a 10A diode operating at 125'C
From a van.I don't know if your car charge cable is coming from a car battery charger from AC or from a car. I hope the DELTA will pulse and measure the DC Input port for MPPT optimal impedance matching to transfer maximal power. (or some other algorithm) You should call the DELTA tech support to confirm all these assumptions.
It is a van with PV on roof.Summary
I would not use the car DC port unless this is a van that drives around with a PV power panel on top.
Not in the manual but on the website FAQ. AC or DC it states:I also don't know how your DELTA software works but it should choose all the current available from the DC port (green energy ?) before using AC port if the OUTPUT side demand needs power. So the diode is not necessary.
There is a new model Delta 2 where they have changed the battery type, boasting 6000 cycles.I would expect there is a software setting to limit capacity to 80% so that you can get 800 full discharge cycles of life near / at full 100% charge due to the excess voltage used. So a float charge level of 80% is perhaps optimal
Life is reduced by spending time > 80% capacity during CV mode charging and also < 20% capacity (unless deep cycle type) and over temperature.