Thought I'd share this.
I put together a web based dashboard for a cooling system for water cooled brakes on one of the machines I maintain, temp and fow is monitored for 2 brakes and displayed on gauges and a graph.
I had issues with the flow sensors, one worked but the other triggered both sensor readings, after ages fault finding I found that the magnet in one sensor was triggering the hall sensor in both flow sensors, I had them both bolted together to look nice & neat, now they are apart they work fine.
Sounds simple once found, but it wast so obvious beforehand.
 
Sounds simple once found, but it wast so obvious beforehand.
Go figure? Who would have thought? Yeah, sounds simple once found but I never would have thought to look for that. While I doubt I will ever encounter that thanks for sharing, gives pause for thought.