50mV per amp with 1K load (50uA per amp) would be 20,000 : 1 ??
Is that just a safety resistor and there is another load resistor on whatever that part connects to? It just does not look like the whole CT load circuit to me.
1000:1 is a very common ratio, and those are very cheap on such as Aliexpress.
ps. You should never put any power through a current transformer without the correct load connected, or the secondary shorted out. With an open secondary they try to emulate a tesla coil, arc across the terminals or windings and self-destruct.