Normally in N.A. when using equipment, inverters, VFD's etc, shown as 230v L1 & N, all you need to do is use the L1 L2 240vac there is no Neutral used or needed.??
(i.e. The equipemnt does not know the difference.)
You do use the GND however for the earth terminal.
Usually equipment should not know the difference, but inverter is a power source. I am not so deeply involved in power electronics and do not know the code, but for example,
Champion 42451 generator does not connect neutral to ground, but
BG6250E does (see wiring on page 47). Both are sold on Canadian market by major retailers and must have passed safety inspections.
If this hybrid inverter internally connected neutral and ground, powering from BG6250E connecting generator's L2 to inverter's AC IN N would result in dead short.
Thanks
rjenkinsgb.
My schematic in first post may be incorrect. I think those inexpensive Chinese step-down transformers on Amazon, that are rated for 30min of stated load, are actually auto-transformers.
My needs for 110V are small. Most demanding loads will be 110V/15A, one at a time or very occasionally two that would be running from opposite phase. Automatic loads, like well pump and water heater, are 220V.
For now have the 3kVA uncertified transformer, but I think for certifiable installation will need something like
this.
The problem I see is that if L1 and L2 are not evenly loaded, virtual neutral and utility neutral may have different voltage resulting in ground currents.