I assume that you are in the USA, and the power is split phase, so 120 V phase - neutral and 240 V phase to phase.
Does the kiln have connection to neutral, or is it just connected between phase to phase? If the kiln runs reduced power by running some elements on one phase at 120 V then you need to measure both phase wires as they could be taking very different currents at times. One way to do that is with two separate 120 V kWh meters that are rated 26 A or more.
If you don't have a neutral connection, or you only have some low power electronics connected to neutral, you can use a 240 V kWh meter and connect both phases through that.