We have changed almost everything at this point. First let me describe the situation. Let me again deny responsibility for the setup
This is a small machine shop with 5 cncs, and a 200A 1phase supply. First one 15hp phase converter is started. Then a second 30hp phase converter is started in parallel using the made up 3rd leg from the 1st phase converter. There is a 60A breaker between for safety.
Being that the cnc drives don't work the best with phase converters, a 30hp electric motor running off the phase converters is connected to a 40kva 3phase generator that runs 2 of the cncs. The spindles will come up to rpm and load okay, but when decelerating the spindles the drives error out when the rpm drops to the commanded speed.
Here is where I come in.
The generator has a low freq cutout with an indicator led. I noticed it flickered when that happened, and the generator should be more than enough to power 2 lathes let alone one. So we decided that the 30hp motor driving the generator wasn't enough and replaced it with a 50hp motor. We still get the same results.
So I'm wondering if the rpm is not stable enough under load and the voltage regulator is shutting down, or if the regulator isn't fast enough for the large quick current the drives pull. There is a good chance that starting the spindle is done in a different mode than changing the spindle speed. The spindle start has a ramp up function. Where the speed change is probably done in a closed loop mode for cutting and threading functions.