this is a more dangerous fuse...
Mythbusters did article on people using .22 rounds as fuses!
Definitely not a good idea.
And I've first-hand experience of someone using pieces of nails in place or high current fuses, Some years ago I was called to a breakdown, where the table on a vertical borer was blowing fuses if they tried to reverse it.
The electrical cabinet was so tall I had to use a ladder to get to the right area of the control gear. I asked them to start it so i could see what was happening & BANG! One of the contactors exploded right in front of me.
One of the table motor power contactors had a welded pole so when they hit reverse & the other contactor came in, it put a dead short across two phases.
It turned out they had progressively replaced all the fuses in line with the machine as it kept blowing them, from the motor ones in the machine itself through finally to the main power distribution board - with those done the day they called me..
All with whatever chunks of metal they could fit in the holders & literally chunks of 6" nails in the main power board.
A far more common one I've encountered is people replacing semiconductor rated "ultra rapid" fuses with general line fuses, after a fault has blown fuses on a thyristor drive.
It's often caused just by a carbon build-up on the brushgear to the point there is eventually a flashover. With the proper fuses, no real harm done - but with GL fuses the drive is cooked first, then the fuses blow due to shorted thyristors.