sensor control comunication

Status
Not open for further replies.

rjvh

New Member
Hi can sombody explane me a bit about this subject please

as i work with a lot of sensors and control equipment i mainly use the voltage controled ones
standard is 0-10V and 0-5V so far no problems working with them and undesrstand how to manipulate and use the signal

now we do also have a 0-20mA and a 4-20mA sensors

and personaly i don't get the theory completly and do have problems how to handel these signals

these mA sensors are more used where long distance of cable is involved but you will still have a voltage drop over the cable

at the end of the line i think that the current is measured by the voltage over a resistor with a low tolerance and then handled by opamps again as a voltage signal (please educate me if it is not like this)

do I see it right that the power supply for these sensors are much more critical on the occasion of usage than the voltage sensors??

because i don't see differents in power reqirements in the sensor manuals??

while if you take the cable resistance and a given current the power suply have to vary in voltage for every different sensor conected on it unless they have all the same cable resistance

I do see circuits conected with several sensors but i don't see and don't know how they are uncoupled from each other

Thanks for any replies

Robert-Jan
 
Hi can sombody explane me a bit about this subject please

as i work with a lot of sensors and control equipment i mainly use the voltage controled ones
standard is 0-10V and 0-5V so far no problems working with them and undesrstand how to manipulate and use the signal

now we do also have a 0-20mA and a 4-20mA sensors

and personaly i don't get the theory completly and do have problems how to handel these signals
The 4 to 20mA current varies in a direct relationship with the variable you are measuring.
The 4mA is considered as a ZERO signal, the 4mA is the current required by the sensor to make it function.
The 20mA is considered the maximum signal from the sensor.


The 0 to 20mA operates in a similar way.


these mA sensors are more used where long distance of cable is involved but you will still have a voltage drop over the cable
You do have a voltage drop in the cable, also the sensor electronics require an overhead voltage of about 12V. So when you design the power supply you take into consideration the 'sensor' volatge, cable voltage drop and the voltage drop in the 'sense resistor' at the receiver.
The sense resistor is about 250R, thats +5V for 20mA.

at the end of the line i think that the current is measured by the voltage over a resistor with a low tolerance and then handled by opamps again as a voltage signal (please educate me if it is not like this)
Thats correct, a close tolerance resistor, say 250R at 0.1%

do I see it right that the power supply for these sensors are much more critical on the occasion of usage than the voltage sensors??
The psu is not critical, just allow for ALL the voltage drops in the loop.

because i don't see differents in power reqirements in the sensor manuals??

while if you take the cable resistance and a given current the power suply have to vary in voltage for every different sensor conected on it unless they have all the same cable resistance
The resistance of the cable has to such that you leave enough 'voltage for the sensor to operate over its full range.
I do see circuits conected with several sensors but i don't see and don't know how they are uncoupled from each other

You are measuring 'CURRENT' in a LOOP.

Thanks for any replies

Robert-Jan

Hi Robert Jan
Hope this helps, please feel free to ask for more detail, if required...:)
 
Last edited:
Hi eric thanks for the info

is there a sertain standarised resistance in the sensors (like you mentioned 250:eek:hm:)or not
and if there is does the sensor have a voltage regulation build in as that majority of the sensors are feed with 12V to 24V?

Robert-Jan
 
Hi eric thanks for the info

is there a sertain standarised resistance in the sensors (like you mentioned 250:eek:hm:)or not
and if there is does the sensor have a voltage regulation build in as that majority of the sensors are feed with 12V to 24V?

Robert-Jan

hi,
The resistor value of 250R is chosen to give +5V at 20mA, so it can be connected directly to a PIC.
For PIC working with a Vss of 3.3V you would chose a 165R resistor.
Remember the ZERO will be +1V thats 4mA thru the 250R.

If you look at the sensor spec sheet it will say what the Vmin for the supply voltage is, mine have always been 12Vdc.
I used a 24Vdc psu to drive the sensor and the cable, so 12V + 5V across the resistor = 17V... that leaves a permitted drop in the cable of 7Volts.

Knowing the resistance/meter of the cable you can calculate the max length of the cable to give 7V maximum drop.
If required you can increase the psu to say 28V. BUT you must also consider the Vmax the sensor spec states. about 28/30Vdc in my experience.

Does this help.?
 
Last edited:
if you have as in your exsample a permited voltage drop of 7 volt by max sensor output but your voltage drop is max 5V over the cable so there's still 2V left open
you have to adjust this on your power supply or put another resistor so that there is a voltage drop over the "compensation" resistor from 2V

do i understand that good?

Robert-Jan
 
if you have as in your exsample a permited voltage drop of 7 volt by max sensor output but your voltage drop is max 5V over the cable so there's still 2V left open
you have to adjust this on your power supply or put another resistor so that there is a voltage drop over the "compensation" resistor from 2V

do i understand that good?

Robert-Jan
hi,
No, another resistor is not required.
Consider the 'sensor' has a quoted voltage operating specification of 12Vdc thru 24Vdc.
This means the 'sensor' has an inbuilt voltage regulator that can handle 12Vdc thru 24Vdc.

So any 'excess' voltage appearing at the 'sensor' is taken care of by the internal regulator.

Think of the 'sensor' as a LM317 connected as a Constant Current source,say set for 20mA.
If you now connected the LM317 to a variable psu, the constant current would remain
the same over a wide range of input voltages.

Consider now that the resistor thats sets the constant current in the LM317 is able to change, acting as the 'sensor element' then the constant current would vary.

You could measure this change in current by adding a series resistor, say 250R and measuring the voltage across the resistor.

Another important point about 4 to 20mA loops, is the current will still remain the same even if the 250R is now 0R.

If its open circuit, the sensor will not work.
 
Last edited:
water pressure that have to comand VSD and comparators

pressure sensors i use are from DS europe

they have them in all the standard ranges and outputs but
i am constanly looking for other sources as i don't want to rely to much on one suplier(price and delivery reasons)

Robert-Jan
 
water pressure that have to comand VSD and comparators

pressure sensors i use are from DS europe

they have them in all the standard ranges and outputs but
i am constanly looking for other sources as i don't want to rely to much on one suplier(price and delivery reasons)

Robert-Jan

hi,
My company product range was Hydrographic surveying electronics, tidal water gauges [4 to 20mA] , range finder lasers,
depth echo sounders, digitisers,data loggers, radio telemetry..etc.

If I can help, please ask..:)
 
Last edited:
As for sensor outputs that have possibly low power/yield, couldn't you put them into a operational
amplifier with low distortion? Seems like that would work.
 
Last edited:
Hi krumling

sensors in the industry envoirement do use only standarize output so you they are exchange able with other brands and types without that you have to adapt the equipment that it is conected

if you want to use the signal (and in the conected equipment 99% is) i always put it in a opamp just for buffering if i want to swich on the signal or re distribute it to more devices

Robert-Jan
 
Ok thanks a lot, that helped solve a few conundrums.
 
The 4-20ma analog instrumentation standard was developed for the petro-chemical industry many decades ago.

The thing to remember in these kind of instrumentation 'loops' is that the sensor is an active device that also knows it's output current value and constantly dynamically adjusts it's output to the value it's sensor is measuring. This allow it to be used in wire loops from any distance up to several thousand feet without having to be concerned about the voltage drop in the wire run. The typical measurement resistor at the receiving end is 250 ohms, resulting in a 1 to 5 volt measurement range, however any resistor load can be used to taylor the voltage measurement range desired up to the limit of what the loop power supply voltage can deliver.

As I said the typical 24 vdc loop power can power a loop with several thousands of feet or wire and the 250 ohm load resistor. The reason for the 4 ma 'zero' value (called live zero) is the power generated in the 0-4ma range powers the active circuitry in the sensor (generally called transmitters) and also allows the receiving circuits the ablity to detect a bad measurement value if there is less then 4ma flowing in the loop, say as a result of a broken wire, otherwise it would be impossible to determine if a 0ma signal was an valid active measurement or a open wire. Also a shorted wire loop would result in a larger out of range value of up to 96ma (assuming a 24vdc loop and a 250 ohm load resistor and ignoring loop resistance) that the recieving circuitry could also ignore as being a bad out of range measurement value.

The 4-20ma standard is a very robust, reliable, accurate and well known method of measureing remote sensors. The main disadvantages are that each measurement loop requires it's own dedicaded wire pair and that the sensor requires active electronics devices at the sensor end of the loop. These kinds of sensors (industrical process transmitters) typically cost many hundreds of dollars (and up) but were designed for continous operation in very harsh enviroments.

Lefty
 
Last edited:
These kinds of sensors (industrical process transmitters) typically cost many hundreds of dollars (and up) but were designed for continous operation in very harsh enviroments.

Lefty

Yep that's right they are not cheap :(

Thanks for your educating reply.

Robert-Jan
 