Sensor

Status
Not open for further replies.

chandu13

New Member
hi

iam measuring the vacuum using vacuum sensor and displaying on the controller.

For 0v=10bar, 1v=20bar, 2v=30bar, . . . 9v=90bar, 10v=100bar

When I removed sensor from controller it is showing 10bar (0v) on the display.

How to do when I removed sensor from controller it should display “SENSOR OPEN”.

How to detect weather sensor is connected to the controller or not .

Regards
nari
 
chandu13 said:
hi

iam measuring the vacuum using vacuum sensor and displaying on the controller.

For 0v=10bar, 1v=20bar, 2v=30bar, . . . 9v=90bar, 10v=100bar

When I removed sensor from controller it is showing 10bar (0v) on the display.

How to do when I removed sensor from controller it should display “SENSOR OPEN”.

How to detect weather sensor is connected to the controller or not .

Regards
nari

Assuming you are using an analog input to the controller and that 0 volts is a valid in range value, then a typical way to detect a 'loss of sensor' is to bias the input with a very high resistance to a 'top of scale' voltage, so called 'upscale burnout' and have the software logic detect this higher then full scale value as an invalid measurement. That means you will have to define in your software what the highest valid value will be and bias the input to something higher then that but still within the A/D measurement span. You will have to research the impedeance of the microcontroller's input and the sensor's output impedenace to determine the bias resistor's value.

Lefty
 
chandu13 said:
For 0v=10bar, 1v=20bar, 2v=30bar, . . . 9v=90bar, 10v=100bar
Where did you get those figures from?

Did you pluck them out of thin air or are they from a datasheet?

I don't see how you can measure a vacuum as high as 100bar (unless you're 1km under water) because the pressure on the earth's surface if only 1bar.

You don't normally measure the quality of a vacuum in bar, you normally use pascals, torr or millibars.
 