I've got a 2021 e-UP which is supposed to accept charge at 7 kW with a type 2 IEC 62196 connector, but it's only running at around 3.6 kW.
I've got a Rolec WallPod charger, labelled 32 A, which is around 7 KW at 240 V.
The current was measured with a clamp meter, and by timing the flashes of the little light on the supply company meter. 3.6 kW agrees with the estimated time to full charge that the car displays, given the size of the battery and the amount of charge shown on the gauge.
I've checked the 1 kHz PWM signal from the EVSE to the car, and that has a duty cycle of just over 50%, which seems to be about right to tell the car that it can take 7 kW. I've attached a screenshot from the oscilloscope.
The charging cable has 220 Ohm resistors between ground and the PP connection at each end.
Any ideas why I'm only getting 3.6 kW?
I've got a Rolec WallPod charger, labelled 32 A, which is around 7 KW at 240 V.
The current was measured with a clamp meter, and by timing the flashes of the little light on the supply company meter. 3.6 kW agrees with the estimated time to full charge that the car displays, given the size of the battery and the amount of charge shown on the gauge.
I've checked the 1 kHz PWM signal from the EVSE to the car, and that has a duty cycle of just over 50%, which seems to be about right to tell the car that it can take 7 kW. I've attached a screenshot from the oscilloscope.
The charging cable has 220 Ohm resistors between ground and the PP connection at each end.
Any ideas why I'm only getting 3.6 kW?