The circuit is NOT usable to feed power to the Vac, What you have here is a synchronized rectifier but the opposite IGBT antiparallel dione turns on too-- causing a short.
You can not use square waves to feed power to the grid, you need to have a sine wave equal to the grid sinewave and phase synchronized -- in reality you need a DC/AC inverter with a Pure Sine wave with variable level to be just higher just enough to place the current direction toward the GRID .
The basic circuit is quite critical because it needs to detect the Grid drops to automatically disconnect from the Grid -- this to avoid electrocuting the workers trying to bring the Grid power up.
ALSO you need to detect the current to insure that the system is in phase with the Grid to have a very high power factor .
The companies that are manufacturing Grid tied Inverters try to keep their schematic design quite SECRET.