loss of neutral at 50ms..note sudden jump in ph-Neut voltage.
This is from sim of #19 above
Except he's asking about UK single phase supplies to domestic premises - so only two incoming wires, neutral and live - if either is disconnected you get no power at all.
Industrial three phase is somewhat different, and can be connected as either star or delta - where delta has no neutral at all. But any three phase system should have little current through the neutral anyway, as it's supposed to balanced across all three phases as much as possible, hence thick live wires and only a thin neutral.
Is'nt this the question?For a 10kW installation, supplied with three phase, how can we ensure that the Line-Neutral voltage does not rise up to the line-line voltage if there is a loss of neutral connection?