Good call, I'm re-using the old tacho so the connections will be the same, however I plan to run the mot uncoupled to make sure of direction, I cannot risk going backards.
Yes the field has its own bridge rectifier, 2 of the diodes are scr's, the gates go to the drive, it controls the o/p, theres also a choke in series with the field, we have to replace this, as the field voltage/current isnt the same, the old motor has a 200v 24a field, the new is 155v 46a parallel connected 310v 23a series, our controls supplier has stated we should apply 108v to the field in parallel, one thing I'm trying to get an answer on is they implied the choke drops the voltage to 108v, however the rectifier is scr controlled so the drive will be able to regulate voltage, and would make more sense, sounds like the supplier doesnt know or has a lack of communication somewhere.
Not knowing the voltage or power factor involved I cant just do an inductive reactance calc on the field choke.
As per usual I end up waiting & being messed about by suppliers, the motor shows up tomoz, glad we only paid a deposit, also glad their commissioning engineer is signing the ticket after we've fitted it, however he'll need the correct stuff here & fitted before his bit can be done, yes I tried talking with this geyser but get the runaround every time and not got through.