Hi darkfeffy,
Are you sure all the info you provided is correct? The reason i ask is because
your flow graph comp network equation looks like it is missing something, and
your other equation looks like it has a rather large constant term. So, how
did you come up with the equation for your plant? Also, is there a complete
circuit we can have a look at? And how did you get only a first power of 's'
in your compensator equation when there are two active elements in it
in the schematic?
This is very important because if we get the
wrong information we can never offer a good suggestion.
Right now it looks as if your plant is not controllable, but if you are working with
a relatively common circuit then my guess would be that the equation was
not extracted correctly.
Hi MrAI,
Here is how I came up with the compensator.
1. I calculated the control-to-output transfer function for the ideal boost converter. Using section 8.2.2 of “Fund of Pwr Electronics” with the following parameters:
Vin = 42V; Vout = 189V; Power = 4170VA; L = 1mH; C = 1000uF.
I obtained Gvd (please see picture 1 – I do not know how to insert a photo directly in the text).
2. Obtained the transfer function of the duty cycler. Simply used 1/Vm where Vm is the valley-to-peak voltage of the ramp. The UC3823n has Vm = 1.8V.
3. Obtained the feedback gain H(s) as 1/74. Voltage divider circuit which should give 2.55V when output is 189V.
4. For now, I used no compensator i.e. Gc(s) = 1.
5. Plotted the root locus of the uncompensated system with these parameters (please see picture 2). As expected, there is a RHP zero at 1.3kHz and two complex LHP poles at 35Hz. The system is UNSTABLE (because there are loci in the RHP).
6. I set the design objectives as: Settling time < 0.05s; overshoot < 5%.
7. Compensator design starts:
a. Inserted a pole very near the RHP zero. This has the effect of cancelling the loci in the RHP. I chose a RHP pole at 1.326 kHz.
b. Inserted a zero in the LHP. This has the effect of “pulling” the root locus towards the left. I chose a LHP zero at 122 Hz.
c. As of now both these actions result in a compensator with a unity gain.
d. Noticing that the closed-loop poles were not really satisfying the design objectives (settling time and overshoot), I moved them till they satisfied these objectives. This gave a gain of 3.055 (i.e. 9.7dB).
e. Please see picture 3 for the overall compensated system showing the design objectives.
8. Using a note from Texas Instruments (I posted it earlier in this thread. It is called “Topic 3”), I designed the compensator components as shown in picture 4.
I wish to add that unlike what RCinFLA thinks, I am not testing at 4kW yet. I am using a much reduced model. In fact during testing, the ONLY load was the voltage divider at the output. I was thinking that if the control system works for a little model, it should perform as well for a larger model (if working with the same circuit params). I also want to master the design of such control systems so as to modify circuit parameters and still obtain desired results.
Please point out all errors I made (this is certain because the control system did not work) and suggest a methodology. Thanks for your useful suggestions and remarks.
Edwin