Telephone companies only use 48V because it's the highest voltage that's still reaonably safe.
Why did you go for 12V? 48V would have been much better as it would only use 130A rather than 520A, assuming 80% inverter efficiency.
The red batteries appear to be two cell units which will be connected in three paralleled series banks for 48V. This is odd because normally you can buy high capacity single cells but not two cell modules.
Why did you go for 12V? 48V would have been much better as it would only use 130A rather than 520A, assuming 80% inverter efficiency.
The red batteries appear to be two cell units which will be connected in three paralleled series banks for 48V. This is odd because normally you can buy high capacity single cells but not two cell modules.