1. Transfer connection - Like one of these?**broken link removed**
2. Before you get really involved, just re-route the connections DIRECT to the furnace only from the L14-30 and verify that the N and ground continuity exists at the generator. I would suspect the furnace will work. You can wire nut the connections and it would be nice if you could include a fuse/breaker rated for the furnace. You also have the disconnect at the furnace.
e.g. Get a fuse and lamp socket, wire it in series and wirenut to the incoming power with the switch off. Verify the voltages L-N and L-G and N-G at the furnace and ten throw the switch at the furnace. Bet it will work.
We don;t get may generator questions here.
3. Ideally, you have to break the ground/neutral bond at the generator. This might be tough to do. Run the independent ground back to the ground rod if possible and the neutral back to the neutral.
4. Hopefully, your neutrals and grounds are separate in the transfer panel.
The independent test, should rule out generator compatibility.
What I would say is, that some people make a L14-30 plug and just connect the ground and neutral together in the plug once they have disconnected the ground-neutral bond in the generator. Most people don't need 240 V portable power, so it's a good solution. So, when you need to use the 120 V as portable power, just insert the plug.
2. Before you get really involved, just re-route the connections DIRECT to the furnace only from the L14-30 and verify that the N and ground continuity exists at the generator. I would suspect the furnace will work. You can wire nut the connections and it would be nice if you could include a fuse/breaker rated for the furnace. You also have the disconnect at the furnace.
e.g. Get a fuse and lamp socket, wire it in series and wirenut to the incoming power with the switch off. Verify the voltages L-N and L-G and N-G at the furnace and ten throw the switch at the furnace. Bet it will work.
We don;t get may generator questions here.
3. Ideally, you have to break the ground/neutral bond at the generator. This might be tough to do. Run the independent ground back to the ground rod if possible and the neutral back to the neutral.
4. Hopefully, your neutrals and grounds are separate in the transfer panel.
The independent test, should rule out generator compatibility.
What I would say is, that some people make a L14-30 plug and just connect the ground and neutral together in the plug once they have disconnected the ground-neutral bond in the generator. Most people don't need 240 V portable power, so it's a good solution. So, when you need to use the 120 V as portable power, just insert the plug.