I got a transformer that is 25-25-0 plus 12-12-0, both em are dual output i need to know if i can just connect em in this same order to get more voltage ik, at the end the total watts will be the same, and if that's possible, is this safe?
It means that, if the current rating of one of the windings is 4 Amps, and the other winding is rated at 10 Amps, you can only run the series connection at the lower of the two, or 4 Amps. The two windings referred are the two isolated windings.