Here's the proposed add-on Fault Sensor Module (FSM) for detecting the situation that Vt is high (i.e pump nominally on) but there is no pump current. (With hindsight a variation of it it could also have been used to detect a locked rotor but with pump drawing current.....but we won't go there )
View attachment 68771
Operation
U1 is a quad op-amp so can handle 4 pumps. Each amp is used as a comparator, comparing the individual voltage Isense with a common 140mV reference derived by R1/R2. Consider the first section. Providing pump 1 current (pulsed or continuous) exceeds ~0.5A (Isense1 > 140mV) the amp output is low, discharging C3. If current fails then C3 charges (providing Vt1 is high) and signal Fault1 rises above 7V (the upper Schmitt threshold of gate U1d in the PDM) in ~ 1.2s and operates the alarm.
If this module is used with paired pumps then one Vt control signal (from U3c of the timer) should be fed to two of Vt1-Vt4 and the other Vt signal (from U3d of the timer) should be fed to the other two. Each PDM will need its own Fault input signal.
Re the alarm set-up, I think you've presently got multiple sounders, Joe?
Way back when, I did post a "Tidal-timer, Power, Alarm and Speed-set Module (TPASM)" which combined various alarm inputs to drive a common sounder, but lit individual alarm LEDs.
View attachment 68771
Operation
U1 is a quad op-amp so can handle 4 pumps. Each amp is used as a comparator, comparing the individual voltage Isense with a common 140mV reference derived by R1/R2. Consider the first section. Providing pump 1 current (pulsed or continuous) exceeds ~0.5A (Isense1 > 140mV) the amp output is low, discharging C3. If current fails then C3 charges (providing Vt1 is high) and signal Fault1 rises above 7V (the upper Schmitt threshold of gate U1d in the PDM) in ~ 1.2s and operates the alarm.
If this module is used with paired pumps then one Vt control signal (from U3c of the timer) should be fed to two of Vt1-Vt4 and the other Vt signal (from U3d of the timer) should be fed to the other two. Each PDM will need its own Fault input signal.
Re the alarm set-up, I think you've presently got multiple sounders, Joe?
Way back when, I did post a "Tidal-timer, Power, Alarm and Speed-set Module (TPASM)" which combined various alarm inputs to drive a common sounder, but lit individual alarm LEDs.