This is not a field-regulated alternator and the AB20L datasheet specifies the source must be 5 HP or the warranty is void due to damage from delays in thermal protection. Air pressure power, I believe is the product of pressure (P)* air flow volume (V).
The no-load V/f should be constant and the max load power should be at 50% max RPM.
But I recall they rate max at power 60 Hz.
What is the [psi / watt] at 33 Hz.
| | | | | | Pwr Max= | 2400 |
PSI | V [volts] | I [Amps] | f [Hz] | psi/VA | f / fo | Pwr [W] | P / Pmax |
150 | 55 | 0.9 | 33 | 3.03 | 89% | 49.5 | 2.1% |
170 | 78 | 2.1 | 33 | 1.04 | 70% | 163.8 | 6.8% |
190 | 112 | 4.1 | 33 | 0.41 | 56% | 459.2 | 19.1% |
| | | | | | | |
PSI | V [volts] | no load | fo (Hz) | V / f | | | |
150 | 85 | “0” | 37 | 2.30 | | | |
170 | 168 | “0” | 47 | 3.57 | | | |
190 | 235 | “0” | 59 | 3.98 | | | |
Conclusion not enough Prime Mover source power to generate 2400 VA out at 190 psi. perhaps suboptimal torque conversion 1:1 and needs pulleys. Or better use a field regulated Alternator.